Not sure, it shouldn't be. the blending valve on the UFH is brand new, I assume it is thermostatic. I've got it set to 45°C flow currently so as hot as I can get it really.IF starting up say a 5kw UFH from cold that normally runs with flow/ return temps of 45C/37C and assuming a boiler flow temp of 65C, then the flow through the boiler should be 8.96LPM with a dT of 8C, once up to temperature then the flow through the boiler will only be 2.56LPM with a dT of 28C, the remainng 6.4LPM will be recirculated through the UFH manifold so can understand if the boiler was tripping on a high dT with UFH up to temp but difficult see it tripping on UFH start up except the TMV is stuck in one position?
I guess I can get the pump datasheet so find out what the flowrates are at the different speed settings, & set it to the above. Honestly 7 poxy radiators and an UFH system in a house should not be this difficult. I design controls for commercial building, but the boilers at least do what we ask them, rather than these domestic pre-set routines.