Very old henley fuse box

That surely depends upon whether one is writing a Standard in terms of metric or imperial units? - '3 metres' is a pretty round number for a metric one. I wonder if any of these "3m requirements" pre-dated metric versions of the Standards - if they existed in, say, 'imperial' versions of BS7671, I would suspect that the figure may well then have been 10 feet.
Which I think in return, is stillp's suggestion. That 3m predates the use of metric measurements.
 
Sponsored Links
Sorry, I was replying to BAS. Yes, I'm agreeing with you - I don't think your post was there when I started typing. Great minds think alike, as they say.
Indeed they do appear to, on this occasion! [but did it really take you 34 minutes to type a 2-line post? :) ]
Yes, the arbitrary 10 feet was used before we went metric...
As I suspected - so as 'round' figures as were possible under both imperial and metric regimes!

Kind Regards, John
 
Sponsored Links
One hears of DNOs complaining (or worse) about 'unprotected' meter tails a little more than 3m in length
Does one?

Does one hear it directly, or as as a many-steps-removed rumour?

Does one have any real evidence?


The requirement is to operate the cut-out fuse within 5 sec for a fault on the tails or CU prior to the first point of the customer's protection (which is where the .8 Ze figure comes from, this may vary in some DNOs that install smaller fuses than the 100A we use.
Indeed.

But that 5s time applies in BS 7671 to all final circuits which do not serve portable equipment. And the tails from the meter are part of the consumer's installation, not the DNOs, and "have to" comply with BS 7671.

Is there a 3m limit formally specified in the ESQCR or in the contract the consumer signs?

If not, then as long as the Zs at the CU incomer is such that the fuse will operate in 5s, can a DNO insist on something different?
 
One hears of DNOs complaining (or worse) about 'unprotected' meter tails a little more than 3m in length
Does one? Does one hear it directly, or as as a many-steps-removed rumour? Does one have any real evidence?
Well, one does 'hear of' these things happening, but your second two are very good questions - it can be very hard to distinguish between fact and 'urban myth' these days! However, in context, I don't think that even westie is denying that DNOs do (and have done for a long time) have (and therefore presumably sometimes' impose'/'enforce') a "3m rule".
The requirement is to operate the cut-out fuse within 5 sec for a fault on the tails or CU prior to the first point of the customer's protection (which is where the .8 Ze figure comes from, this may vary in some DNOs that install smaller fuses than the 100A we use.
Indeed.
You say 'indeed'- but, as I've pointed out, even with tails of zero length/impedance, one cannot satisfy that requirement if Ze is above about 0.38Ω - so there appears to be something a bit wrong with (or unworkable about) that 'requirement'!

Kind Regards, John
 
Is there a 3m limit formally specified in the ESQCR or in the contract the consumer signs?

In effect it forms part of our T&Cs for a new or altered supply
See the specification below for out door meter reading facilities where it states

Customer's switches on inside wall within 1800mm of meter board

Which is the actual requirement, we though have always had discretion to extend that distance to allow for a maximum length of tails of 3m.

What would we do it the customer could not meet that requirement? Not install the supply (or move the meter)

http://www.enwl.co.uk/docs/connections/guidance-for-outdoor-meter-reading-facilities.pdf


Does one hear it directly, or as as a many-steps-removed rumour?

Within the DNO (and Electricity Board prior to that) I work for it is a fact. One that I've worked to for nearly 40 years!!

This also has some useful information

http://www.enwl.co.uk/docs/connections/guidance-for-meter-board-layout-for-domestic-connections.pdf
 
But that 5s time applies in BS 7671 to all final circuits which do not serve portable equipment. And the tails from the meter are part of the consumer's installation, not the DNOs, and "have to" comply with BS 7671.
If one takes that view, then do you feel that an immediately-pre-CU OPD should always be installed in those cases in which Ze is too high (>~0.38Ω or whatever) for the cutout fuse to provide disconnection times (for faults in meter-CU 'tails') which would satisfy BS7671?

Kind Regards, John
 
I can really understand the 3m rule. If, like us, you have a DNO supply, then goes up to in between the floor void, then down to above your lounge door, then 3m will cover it. (LA property, and before anyone bites my head off, all beds occupied, full rent paid, not all buying our house on govt. handouts!!).

It was the rather odd route (regards length) that I was querying. But Hey!! I know where it is, I won't be drilling there!!

N.B. Soz for drifting off topic!
 
N.B. #2 I'm finding this a very interesting and informative post. Has any bickering really occurred??? When may it start again?????
 
I can really understand the 3m rule. If, like us, you have a DNO supply, then goes up to in between the floor void, then down to above your lounge door, then 3m will cover it. (LA property, and before anyone bites my head off, all beds occupied, full rent paid, not all buying our house on govt. handouts!!). It was the rather odd route (regards length) that I was querying. But Hey!! I know where it is, I won't be drilling there!!
It would probably make more sense if, rather than worrying about length, they simply prohibited meter-CU tails being 'concealed' (except, I guess, where inevitable to pass through walls) and/or installed in 'vulnerable' positions/locations (per someone's judgement,I suppose!).

Kind Regards, John
 
He's a comic actor¹ - that's what the part requires him to do, and he's well paid for it.




¹ or so we are led to believe - personally I have doubts about both of those labels.
 