Im looking at the voltage in my house, and seems on the high side.
My UPS reports an average of 244V, some peaks of 248V for hours at a time.
The concerning thing is the UPS is on the end of a radial, wired in 2.5mm T&E, approx 15m cable run from the CU.
By my calculations, there is an approx 4v drop on the length to the end, meaning the voltage at my CU 248V on average, with 252V at peak times.
this is JUST under the max of 253V, as I understand it, can anyone confirm my calculations.