Put into simple terms the system has such a large volume that when starting up there is so much cool water returning to the boiler that the differential remains high for longer than the boiler is programmed to expact so it thinks there is a fault.
There is a simple work around to your problem.
As its a large system it should be devided into several zones and the UFH is a typical example.
All you need to do is to seperately time part of the system so that it does not all start at vthe same time ( or put a few minutes delay into part ).
In any case the UFH should be timed to start an hour or more before the rest of the system as it takes longer to warm up.
Tony
It is set at 80c currently.What is the flow temperature when the house is up to temperature?
The problem still occurs, even if I lower the flow temperature.What happens if you reduce the max flow temperature from 80 to 70?
Yes, the pump runs whenever there is demand from the heating controls, so even when the boiler is in slow S53 mode, the pump runs. (This rapidly brings down the flow temp from the boiler.)When the boiler goes into slow mode with S53 showing, does the pump continue to run? How long does it take before it goes back to normal?
There is no stat for the rads! There are indepedent stats for all the rooms with UFH, but the rads just rely on the timer in the heating controls.TRVs on all rads?? Don't you have one rad without a TRV where the room stat is located?
Dont fit a magna or an alpha variable speed pump this will cause the same problems due to the pump modulating down for the load,the boiler wiil see this as an increase through the HEX and trigger S53.
Fixed speed pump UPS25-80.
as previously posted id go with the UPS25-80 or UPS25-100(lowest pump setting)
I've been reading through the spec of the pumps, I seem to have two choices. I want to get about 2.5m^3/hr flow at a 5m head. (To give approximately at 15c temperature differential across the boiler.) The figure for the head is derived from current pump performance graph - see post by D. Hailsham on page 1 of this thread.
ups25-80 will surfice based on your original posted figures.The magna will still give problems during pump modulation with your boiler product and isnt cost eefctive.
What F&R temperatures is your boiler achieving when system up to temperature?
About 20c - when it is up to temperature flow is 80c and return is 60c.