If you read his post carefully he says that he reduced the output to 7kW, which is almost at the bottom end of the modulation range. He has not said if he resolved this problem. I suggested he set it to 35kW.Another odd feature is that he says he has tried to reduce the max output but the boiler does not seem to accept the instruction.
I agree all TRVs should be open and the flow resistance is the minimum. But, if the rads have not been balanced properly they will start closing too early, before the ABV comes into operation. This will result in a reduction in the flow rate and hence an increase in the system pressure.Agile said:At startup the whole system is cold and the TRVs all open thus giving the lowest flow resistance.
To set an ABV to be passing at that setting would mean the full boiler output would never be obtained.
I would like to know why the OP thinks the system is properly balanced.
Did anyone notice this?
So what turns the boiler off when the rads get up to temperature? All the TRVs will have closed, but the boiler will continue to run until something stops it - normally the boiler thermostat, but could an S53 also occur?The OP said:There is no stat for the rads! There are independent stats for all the rooms with UFH, but the rads just rely on the timer in the heating controls.
Might be a good idea if the OP fitted a room stat (and got rid of one TRV).
The maths is OK but a system head of 5.6m, excluding the boiler, is very high. It implies that the pipe have not been properly sized for the heat flow. Assuming you have 38kW at 80/60 at the start, and a flow rate of 1.63m³/hr, your main boiler connections should be 28mm. This will give a pipe velocity of just under 1m/s which is acceptable. But the rest of the system needs to be properly sized as well.The OP said:Right - on that rule of thumb:
Boiler pressure loss = 4.0m (from manual)
Rest of system pressure loss = 2.9m * (1.6/1.15)^2 = 5.6m
Total pressure loss = 9.6m
A proper calculation of the index circuit would help.