The neutral to neutral bar clearly comes from RCD so those two wires just above the MCB's must feed the RCD from the isolator.
With so little on the CU I would start with Isolator or RCD off and test there to start with, with enough power to trip an MCB the problem has to be bad, so no need of insulation tester, multi meter good enough, with all unplugged and MCB's off three readings, earth to neutral, earth to line, and line to neutral, should all be open circuit, but will guess line to neutral is short circuit, if neutral to earth short circuit then likely RCD would have tripped not MCB, but although we would normally test both the line and neutral, if one can remove the neutral wires then one can likely locate the area of fault by disconnecting neutral in centre socket, and neutrals in CU and work out what side fault is.
With so little on the CU I would start with Isolator or RCD off and test there to start with, with enough power to trip an MCB the problem has to be bad, so no need of insulation tester, multi meter good enough, with all unplugged and MCB's off three readings, earth to neutral, earth to line, and line to neutral, should all be open circuit, but will guess line to neutral is short circuit, if neutral to earth short circuit then likely RCD would have tripped not MCB, but although we would normally test both the line and neutral, if one can remove the neutral wires then one can likely locate the area of fault by disconnecting neutral in centre socket, and neutrals in CU and work out what side fault is.