I agree, at present it's all "there might be a potential small problem" and "it might actually be measurable".
Quite, at least in terms of what I am apparently allowed to know. Stillp keeps suggesting that there are 'facts' (which could include information relating to actually measurable problems), but will not or cannot tell me what they are.
On thermal grounds, I have a hard time thinking that it could be an issue.
So do I, but stillp would probably say that is due to my ignorance of 'the facts' and the engineering principles concerned. There could possible be some issues with adjacent MCBs 'running hot' (see below), but I find it very hard to believe that MCBs of same rating, compliant with the same Standard(s) and carrying the same current, but from different manufacturers, will differ appreciably in that respect.
...If it were an issue, then there's be a big problem with having some breakers under constant heavy load (and hence running warm) next to other breakers.
To be fair, manufacturers do acknowledge this potential issue. For example, Wylex say:
Wylex said:
Adjacent thermal-magnetic MCBs should not be continuously loaded at or approaching their nominal rated currents when mounted in enclosures. It is good engineering practice to apply generous derating factors or make provision for adequate free air between devices. In these situations, and in common with other manufacturers, we recommend a 66% diversity factor is applied to the MCB nominal rated current where it is intended to load the MCBs continuously (in excess of 1 hour).
It does not indicate what might 'go wrong' if that 'good engineering practice is not exercised.
So we are down to magnetic effects. Now, a key design point of magnetic circuits is to contain the magnetic field so it goes where we want it - air gaps make for poor circuits. So I would be "somewhat surprised" if there were a significant leakage of field from the trip mechanism - and even more surprised if this, by the time it's jump the gap to the adjacent breaker, it is able to significantly influence the trip in that breaker. ... So a tiny effect, times a tiny effect, times a miniscule probability = what ?
Exactly my point - but, again, stillp will again presumably put my view down to my ('enforced') ignorance.
As as for the thought that a device may change it's characteristics in a meaningful way by being on a metal DIN rail in a tin can with "the wrong sticker" on the front is ... well I'll stay polite and ask for suggestions of realistic potential mechanisms for that.
Quite. Again the the name of remaining polite, I have avoided using words like "ridiculous" but, as I've said, if a protective device were so marginal/iffy that it was "quite likely" to
not perform properly ('safely') if housed in the 'wrong' CU enclosure, I would be
VERY unhappy about having such a device in my house, even if it were in the 'right' enclosure in the company of other 'correct' devices!
Kind Regards, John